@gerald855s posted:

So I've had this unit installed a while. What I like. Being able to to run all of my 115v accessories in the early morning without having to start generator.  We use the 115v microwave and coffee pot usually before 10 am. Most campgrounds prohibit running of generator before 10 am so having the inverter comes in handy. If we do ever run the generator the charger portion of unit has an 80 amp bulk charging function that rapidly recharges batteries way faster than factory inverter. Cons. Size and weight. Yep it's big and heavy but lithium batteries will offset most of the weight. Secondly finding room for it. I was able to reclaim space underneath the sink to fit it into. Overall I love having 115v available all the time and rarely need to run the generator due to our solar system and our trucks 300 amp charging system.

Did you link to the correct unit? Amazon description doesn't indicate a charge function on this one.

Last edited by Eric Dye

Yes, I am aware of that, I have the 2000 watt version. Your initial post shows, and links to, the straight inverter, not the inverter charger that you installed.

Go back and check it out.

I'm interested in changing my current inverter over to something like the one that you used. Not sure yet if I'll stay with another Renogy unit or look into something different. I will say that my current Renogy inverter has served us well, just looking for something with a built in charger. I should have gone that route in the first place.

Nice to see your report on the Renogy unit, thanks.

Sequoia 464 the price has dropped significantly since I purchased mine. The 2000w inverter charger is the same physical size as the 3000w so mainly the weight and output are different. The 80 amp bulk charge especially for lithium batteries is massive. I have my built in converter turnd off it dosen't do lithium batteries anyway. Mine is in a small area under the sink but noise is not an issue. Runs micro and Keurig in the morning flawlessly without having to run generator then solar refills batteries during the day.

@Robert H posted:

I think I have the same unit. It is very heavy. It has a large transformer that provides nice clean sine wave power.

The one thing I don't like about it is you have to turn it on to get shore power. I would prefer that was automatic.

It will run the air conditioner, but not long unless you have a huge battery bank.

I am looking at getting the Renogy 3000w unit this spring.  I was curious why the Renogy inverter needs to turned on to run shore power.  If you have a automatic transfer switch why the inverter has to be on to get shore power.  Maybe I am not understanding how most inverter setups are designed, but I thought it was not necessary.  Thanks

MarkV

I am looking at getting the Renogy 3000w unit this spring.  I was curious why the Renogy inverter needs to turned on to run shore power.  If you have a automatic transfer switch why the inverter has to be on to get shore power.  Maybe I am not understanding how most inverter setups are designed, but I thought it was not necessary.  Thanks

MarkV

It depends on how its installed; if you have an automatic transfer switch it implies you are keeping your existing converter so you can still get 12v and charge the batteries. Basically the shore power line will go directly to your inverter/converter. That is tied into your 12v bus so it can charge the batteries. What you are saying is that the line would go into a transfer switch which would then either go to the inverter/converter, or to the old converter.

Before deciding you want to go that route, make sure Renogy doesn't have some way of setting it to "charge only". My Victron has a 3-way switch for On | Off | Charge Only. And even then, I keep it on 100% of the time because it's controlled via a remote switch / screen where I can set the software to enable or disable inverting. I did remove the converter that came with my trailer, the Victron is on duty; I have to think the Renogy should have similar functionality.

I bought a transfer switch from Progressive Industries which has terminal markings SHORE and GENERATOR. In my case, I would have hooked my transfer switch in the middle of the shore power circuit. Then, I would have connected the inverter output to the generator. With this, if powered into shore with your plug, everything is as it is now. If you were to power up your inverter when on shore, the transfer switch would drop shore power and you would be on inverter. That's the default.

I decided not to use a transfer switch at all, but recreated a shore power plug in my spare battery box. So when I boondock, I take my 30 amp shore power plug and plug it into my battery box plug, turn off the breaker on the on board converter (very important or you create a loop that drains your battery).

I have in the same battery box a 20 amp power input into my inverter. So if I need to say use the generator to charge my batteries, I can do that. I do this because my charge circuit in my inverter is superior to any onboard combined RV converter unit made. I can select my charge voltage and charge current levels. My low frequency inverter is set up as an UPS (uninterrupted power supply)

I am looking at getting the Renogy 3000w unit this spring.  I was curious why the Renogy inverter needs to turned on to run shore power.  If you have a automatic transfer switch why the inverter has to be on to get shore power.  Maybe I am not understanding how most inverter setups are designed, but I thought it was not necessary.  Thanks

MarkV

Mark, I had a 2000 watt Renogy - just an inverter, no charger - the only wiring connection from it was AC wiring going into my stand alone PD ATS. I did not need the unit turned on with shore power.

I replaced that setup recently with a Kisae 2000 watt inverter/charger with a built in ATS. Wiring is different now of course with an AC line to and from the unit. The Kisae automatically powers up when I'm on shore power, I'm figuring that it needs to monitor the juice running through and turn on/off fans as necessary.

I was expecting a simple pass through, but I can see why the unit needs to be on.

@Myl posted:

It depends on how its installed; if you have an automatic transfer switch it implies you are keeping your existing converter so you can still get 12v and charge the batteries. Basically the shore power line will go directly to your inverter/converter. That is tied into your 12v bus so it can charge the batteries. What you are saying is that the line would go into a transfer switch which would then either go to the inverter/converter, or to the old converter.

Before deciding you want to go that route, make sure Renogy doesn't have some way of setting it to "charge only". My Victron has a 3-way switch for On | Off | Charge Only. And even then, I keep it on 100% of the time because it's controlled via a remote switch / screen where I can set the software to enable or disable inverting. I did remove the converter that came with my trailer, the Victron is on duty; I have to think the Renogy should have similar functionality.

Thanks for the response and excellent comments on what I need to check on with Renogy.  The reason for choosing the Renogy inverter is I already have a Progressive Dynamics converter w Li Charging capability and wanted to keep using this unit if possible.  I also was wanting to save some $$ in choosing the Renogy inverter vs. the Victron Multiplus since I am not sure I would use all of the Multiplus functions.

My current system consists of 2BB LiPO4 batteries, which I plan to expand to 4BB, Victron 100/30 Victron SC along with Victron Battery monitor. 

Here is a link to the Renogy 3000w Inverter.

Renogy 3000 w Inverter

Dan as you mentioned I guess it depends on how everything is connected.  Based on the YouTube videos I have watched, the Auto Transfer Switch would do what you mention above.

Hoping to remove our RV cover next week to begin doing spring de-winterizng and starting to look at how to begin my inverter setup.

Thanks

@Marky Mark posted:

I bought a transfer switch from Progressive Industries which has terminal markings SHORE and GENERATOR. In my case, I would have hooked my transfer switch in the middle of the shore power circuit. Then, I would have connected the inverter output to the generator. With this, if powered into shore with your plug, everything is as it is now. If you were to power up your inverter when on shore, the transfer switch would drop shore power and you would be on inverter. That's the default.

I decided not to use a transfer switch at all, but recreated a shore power plug in my spare battery box. So when I boondock, I take my 30 amp shore power plug and plug it into my battery box plug, turn off the breaker on the on board converter (very important or you create a loop that drains your battery).

I have in the same battery box a 20 amp power input into my inverter. So if I need to say use the generator to charge my batteries, I can do that. I do this because my charge circuit in my inverter is superior to any onboard combined RV converter unit made. I can select my charge voltage and charge current levels. My low frequency inverter is set up as an UPS (uninterrupted power supply)

Thanks Dean.  What I am thinking at this time is running the 120 AC line from the Renogy Inverter to the Progessive Dynamics converter, at the same location as my current shore power connection is going to.  That's is what I am currently thinking, but it could change.

Mark V

@sequoia464 posted:

Mark, I had a 2000 watt Renogy - just an inverter, no charger - the only wiring connection from it was AC wiring going into my stand alone PD ATS. I did not need the unit turned on with shore power.

I replaced that setup recently with a Kisae 2000 watt inverter/charger with a built in ATS. Wiring is different now of course with an AC line to and from the unit. The Kisae automatically powers up when I'm on shore power, I'm figuring that it needs to monitor the juice running through and turn on/off fans as necessary.

I was expecting a simple pass through, but I can see why the unit needs to be on.

Ron, I was anticipating wiring the Renogy unit like you mentioned in the first paragraph.  I do have to contact Renogy for some additional questions based on some above comments.

Thanks

Mark V.

In my 1995I did a simple Renogy 2000 installation. I wanted to run my microwave and a second outlet under the TV for my SpringAir mattress pump and miscellaneous other items. I did not want to mess with a transfer switch etc. I am pleased with the Renogy, just make sure you buy one with a remote control switch.

I installed the inverter in the pass thru, vertically on the rear bulkhead. I had Windy Nations make up the cables, includig a 12" one from the positive batery termonal to the fuse. My batteries are on the tongue.I wired heavy cables from the battery to the inverter. Then I cut the female end off of heavy extension cord. I installed a new receptacle next to the existing microwave receptacle. I ran the cut off cord end from the inverter, below thhe trailer in looming, up along the refrigerator , behind the microwave and to the new receptacle.

When I boondock, I simply unplug the microwave and plug iit into the adjacent inverter outlet. I wired a second receptacle below TV.

I istalled the remote swiitch below the water pump switch panel and ran the wires and plugged it into the inverter.

Secured the loom protected wire under the trailer

. System works perfectly, inexpensive and fewer parts to fail.

DO NO FORGET A 12V FUSE NEAR THE BATTERY.

pm any questions, good luck

Initially our inverter was in pass thru, batteries were o tounge. Now upsized 2kw inverter and LFP batteries are under bed. The ATS is behind the breaker panel in the galley. The inverter is switched on via the remote by the door The Inverter feeds the ATS through a 12-3 SO cord running under the trailer alongside the frame. I like the painless auto transfer feeding all the 120 volt appliances. Of course the converter breaker must be off when on inverter.

1500 inverter in passthruinverter in passthru

inverter under bed relocate BB batts old panel

1500 watt inverter under bed (ipgraded 2000watt in same location) remote mounted below fold down table in background.

dist panel BB Inv complete

Almost finished  install

Attachments

Images (3)
  • 1500 inverter in passthru
  • inverter under bed relocate BB batts old panel
  • dist panel BB Inv complete